Re: FOX2001 not operating as intented

페이지 정보

작성일 18-12-12 16:05

본문

Dear Mr. Patrkck,

First of all sorry for the late reply.

We have read your question and we found the problem on your setting.


First press the SET button.

After pressing the SET button the set value is flickering.

And then set 25 for the set value. 


HSP and LSP should not be changed.

Please make HSP and LSP as same as factory setting.


Other settings are fine.

Try as above.

If you have any more question feel free to ask us.


CONOTEC
- Overseas sales team -


 * * * * * Patrick 님이 작성하신 글 * * * * *

 >> Hi! Just gotten a Fox2001 today. Here’s the setting
 >> HSP 25
 >> LSP 24
 >> Typ Col
 >> Dis P
 >> Dif 1.0
 >> Dle 0.00
 >> Cor 0.0
 >>
 >> My understand base on the manual, my compressor should be on when the temperate reaches 25° and compressor off when it chill to 24°. How ever this is not happening. Could your please tell me if my setting is correct.